It's a 2.4 kW oven presently on a 32A mcb. (also 30mA RCD protected).

Circuit is 6.0mm T&E to a DP switch then 3093Y 1.5mm flex to oven.

Installation manual does not specify an OPD value, only that the 'fuse' should not be less than 13A.

Does the 32A mcb need changing for a lower value?
 21 September 2017 02:13 PM
User is offline View Users Profile Print this message



geoffsd

Posts: 1709
Joined: 15 June 2010

Not if the flex can cope with fault current .

Does it really have 1.5 flex attached to the switch? No connector plate below?

I'm surprised the 2.4kW oven did not come with a plug fitted.
 21 September 2017 03:51 PM
User is offline View Users Profile Print this message



mikejumper

Posts: 2418
Joined: 14 December 2006

No plug on oven, that would be my preference anyway at that rating.

No connector plate but flex run neatly in trunking for a short distance horizontally behind kitchen units then buried in oval tube up to to switch. Quite happy with that.
 21 September 2017 04:28 PM
User is offline View Users Profile Print this message



Alcomax

Posts: 231
Joined: 12 November 2009

Odd. 2.2 / 2.4 kw ovens usually state 2.5mm H07 flex in instructions?
 21 September 2017 05:32 PM
User is offline View Users Profile Print this message



mikejumper

Posts: 2418
Joined: 14 December 2006

Originally posted by: Alcomax
Odd. 2.2 / 2.4 kw ovens usually state 2.5mm H07 flex in instructions?

Are you sure, 2.5mm is nominally rated at around 24 Amps.

Even 3kW immersions usually are usually on 1.5mm.
 21 September 2017 07:05 PM
User is offline View Users Profile Print this message



Alcomax

Posts: 231
Joined: 12 November 2009

Originally posted by: mikejumper

Originally posted by: Alcomax

Odd. 2.2 / 2.4 kw ovens usually state 2.5mm H07 flex in instructions?


Are you sure, 2.5mm is nominally rated at around 24 Amps.



Even 3kW immersions usually are usually on 1.5mm.



Maybe so, however a manufacturer can spec what they like.
 21 September 2017 07:08 PM
User is offline View Users Profile Print this message



dustydazzler

Posts: 1362
Joined: 19 January 2016

I recently installed a replacement single oven that came prewired with 1.25mm flex
 21 September 2017 07:19 PM
User is offline View Users Profile Print this message



Alcomax

Posts: 231
Joined: 12 November 2009

Ah it is pre-wired, missed that . It would have had a plug on it originally if it was 1.5mm. If it is flex up yourself, usually manufacturer specs a bigger flex. There must be an odd reason for that.
 21 September 2017 07:53 PM
User is offline View Users Profile Print this message



Fm

Posts: 1714
Joined: 24 August 2011

Make and model?
 21 September 2017 08:37 PM
User is offline View Users Profile Print this message



mikejumper

Posts: 2418
Joined: 14 December 2006

Originally posted by: Alcomax

Ah it is pre-wired, missed that .


No, not pre-wired.
1.5mm flex specified for connection.
 21 September 2017 08:45 PM
User is offline View Users Profile Print this message



mikejumper

Posts: 2418
Joined: 14 December 2006

Originally posted by: Fm

Make and model?


Can't remember, some obscure make I've never heard of that came with the kitchen, as seems to usually be the case with these packaged kitchens.