I want to install an outdoors EV charging point and am trying to understand the regulations laid out in 722.441.4.1.
My interpretation is if I install a sufficiently low impedance earthing electrode attached to the main terminal of the device I can be connected to the PME earthing facility? or does my device need to be installed with its own TT earthing system?
The device should operate at 230V and 16A so using the guidelines this suggests an earthing system with R=6.3 Ohms.
Chris
 03 October 2017 06:26 PM
It's not just the charger load, it is the installation load.
Try this.
Andy B.
 03 October 2017 10:31 PM
Agreed - 6.29 Ohms would be right if the charger was on its own DNO supply. If it was for instance on a 100A domestic, you'd be looking at needing a reliable electrode resistance of about 1 Ohm. (Presuming the EV charger isn't the kind that increases the current drawn when faced with a reduced voltage to keep the power drawn constant, like most switch mode PSUs do ....)