 Undersized cables   - rogerbryant - 03 October 2017 01:21 PM  
 Undersized cables   - KFH - 03 October 2017 02:29 PM  
 Undersized cables   - AJJewsbury - 03 October 2017 02:30 PM  
 Undersized cables   - broadgage - 03 October 2017 04:03 PM  
 Undersized cables   - Zoomup - 08 October 2017 09:14 AM  
 Undersized cables   - broadgage - 08 October 2017 09:33 AM  
 Undersized cables   - sparkingchip - 03 October 2017 03:55 PM  
 Undersized cables   - sparkingchip - 03 October 2017 04:04 PM  
 Undersized cables   - davezawadi - 04 October 2017 10:49 AM  
 Undersized cables   - mikejumper - 04 October 2017 02:06 PM  
 Undersized cables   - Zoomup - 08 October 2017 09:18 AM  
 Undersized cables   - davidwalker2 - 04 October 2017 04:26 PM  
 Undersized cables   - Zoomup - 08 October 2017 09:19 AM  
 Undersized cables   - davidwalker2 - 04 October 2017 04:30 PM  
 Undersized cables   - AJJewsbury - 04 October 2017 04:46 PM  
 Undersized cables   - rogerbryant - 05 October 2017 06:55 AM  
 Undersized cables   - broadgage - 05 October 2017 09:40 AM  
 Undersized cables   - broadgage - 05 October 2017 11:06 AM  
 Undersized cables   - Zoomup - 08 October 2017 09:21 AM  
 Undersized cables   - Zoomup - 08 October 2017 09:25 AM  
 Undersized cables   - AJJewsbury - 08 October 2017 09:42 AM  
 Undersized cables   - Zoomup - 08 October 2017 09:58 AM  
 Undersized cables   - Zoomup - 08 October 2017 09:48 AM  
 Undersized cables   - AJJewsbury - 08 October 2017 10:14 AM  
 Undersized cables   - sparkingchip - 08 October 2017 10:45 AM  
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 03 October 2017 02:30 PM
User is online View Users Profile Print this message



AJJewsbury

Posts: 15812
Joined: 13 August 2003

Would a Zs test show if it was a problem?

Unlikely, unless you happened to know the precise length of the cable (and had a better than average loop tester, especially if on a non-trip setting).

This should confirm that the OPD is correctly sized to protect the circuit.

If might be protected against faults - but not necessarily against overloads (i.e. loads above the actual (reduced) CCC). Even faults might be a bit dodgy as there's a min c.s.a. needed to pass the adiabatic as well as Zs to consider.