 Current Carrying Capacity for 90deg XLPE ref method 100   - synapse - 02 October 2017 04:39 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - AJJewsbury - 02 October 2017 05:07 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - weirdbeard - 02 October 2017 05:57 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - mapj1 - 02 October 2017 07:27 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - synapse - 05 October 2017 10:30 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - ArduinoXR - 06 October 2017 01:22 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - leckie - 06 October 2017 05:23 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - OlympusMons - 06 October 2017 07:37 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - Alcomax - 06 October 2017 08:45 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - leckie - 06 October 2017 09:07 PM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - AJJewsbury - 07 October 2017 08:21 AM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - OlympusMons - 07 October 2017 10:52 AM  
 Current Carrying Capacity for 90deg XLPE ref method 100   - AJJewsbury - 08 October 2017 09:49 AM  
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 06 October 2017 07:37 PM
User is offline View Users Profile Print this message



OlympusMons

Posts: 50
Joined: 05 February 2016

You don't have to increase the csa of the whole cable, just the bits of it that are in contact with the insulation.
 06 October 2017 08:45 PM
User is offline View Users Profile Print this message



Alcomax

Posts: 231
Joined: 12 November 2009

You don't have to increase the csa of the whole cable, just the bits of it that are in contact with the insulation.



That is a whole lot of joint boxes then.

Given that sparky's are the only ones that give a monkeys about de-rating of cables, extra insulation after the event by others cannot be predicted. The only routes of some certainty are sheathed and plastered. Everything else is up for grabs, subject to builders / badgers law.
 06 October 2017 09:07 PM
User is offline View Users Profile Print this message



leckie

Posts: 4323
Joined: 21 November 2008

Yes, I suppose we really should wire lighting circuits in 2.5mm