IET logo
 
IET
Decrease font size
Increase font size
Topic Title: Unexpected dimming of lights.
Topic Summary: Why is it happening when the load is removed?
Created On: 22 September 2017 09:43 AM
Status: Read Only
Linear : Threading : Single : Branch
 Unexpected dimming of lights.   - potential - 22 September 2017 09:43 AM  
 Unexpected dimming of lights.   - kellyselectric - 22 September 2017 12:14 PM  
 Unexpected dimming of lights.   - nad - 22 September 2017 01:00 PM  
 Unexpected dimming of lights.   - mapj1 - 23 September 2017 12:15 AM  
 Unexpected dimming of lights.   - potential - 23 September 2017 10:16 AM  
 Unexpected dimming of lights.   - mapj1 - 23 September 2017 12:32 PM  
 Unexpected dimming of lights.   - OlympusMons - 24 September 2017 02:12 PM  
 Unexpected dimming of lights.   - potential - 24 September 2017 05:41 PM  
 Unexpected dimming of lights.   - potential - 24 September 2017 05:44 PM  
 Unexpected dimming of lights.   - MWalker86 - 24 September 2017 11:10 PM  
 Unexpected dimming of lights.   - kellyselectric - 26 September 2017 12:48 PM  
 Unexpected dimming of lights.   - kellyselectric - 05 October 2017 11:12 AM  
 Unexpected dimming of lights.   - alancapon - 24 September 2017 06:11 PM  
 Unexpected dimming of lights.   - kellyselectric - 24 September 2017 07:52 PM  
 Unexpected dimming of lights.   - potential - 05 October 2017 01:57 PM  
 Unexpected dimming of lights.   - potential - 05 October 2017 02:01 PM  
 Unexpected dimming of lights.   - kellyselectric - 05 October 2017 04:41 PM  
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 24 September 2017 05:41 PM
User is offline View Users Profile Print this message



potential

Posts: 1632
Joined: 01 February 2007

The blower is marked 230 volts, 50 hz, 2.2 kW.
The house earth is exported to the shed via the 3rd core.
The bonding in the house is 10mm and very short, under a metre from the MET to the lead water pipe and gas meter supplied via a steel gas pipe.
The supply cable is very old and relatively small.
There is no connection within the house between the MET and the incoming neutral.
The MET has a 10mm wire running to the supply cable steel sheath.

Using a clamp meter there was less than 6 mA flowing between the sheath and MET.
The load in the house was small (as was the load when the phenomenon occurred) being only 1.65 amps.


I did a few more tests but my wife is out this afternoon so wasn't able to repeat the original scenario.
I did not see any dimming of lights in the house except on switch on. There was no dimming after switch off.
I couldn't check in the shed.
I did run an extension lead from the house socket to the shed but the lights did not dim when the blower was switched off.
(This was as I expected)

I checked what voltage exists between the house neutral and a true earth (screwdriver stuck in the lawn).
It varied as I'd expect, but at the time the voltage was less than 2 volts.
When I applied a 4 kW load via another circuit running directly to the CU this voltage increased to 3.6 volts.
I am aware that the supply voltage to the house varies a great deal, anything between 244 to 207 volts so I will monitor this in relation to the supply voltage in the next few days.