geoffsd
Not quite sure of the point you are making.
Also, I do not see the point of some guidance document written by someone stating solutions to problems which do not exist.
"Non-compliances with the current edition of BS7671 that do not give rise to danger and do not require reporting".
So what? Who says?
It's up to the inspector. If he cannot do the job without a guidance document then he shouldn't be doing EICRs.
I note that in the referred item, they have not addressed the fact that 544.1.2 requires (main) bonding to a part which may not be an extraneous-c-p while leaving unbonded the part which is.
Also, not including "where practicable" which is in that regulation.
Merely copying parts of something is only going to cause more confusion.
Why do they bother?
 27 May 2017 02:00 PM
weirdbeard
Hi geoff, assuming you are reffering to my previous post, I was posting a documentary link to reasonable advice directly concerning the ops question
:beer)
 27 May 2017 03:51 PM
Fm
Must be the falling standards slipping into the network side
I assume you cannot enquire anymore to determine the earthing arrangement?
 27 May 2017 04:09 PM
Originally posted by: NMBelectrical
. . . does that spell the end for reduced size main bonds in any UKPN areas?
What do the DNO say? You are relying on their fuse for the first bit of an installation, so they will have an opinion, which may be given on their website.
My employer (a DNO) require 25mm tails and a 16mm main earth conductor for all supplies at 100A per phase or less, regardless of the earthing type provided. Even for a TT we require the main earth conductor available in a suitable block adjacent to the meter.
 27 May 2017 04:51 PM
NMBelectrical
Stroma is another CPS. In the UKPN document linked by Leckie, they state to treat their whole network as PME and size Main bonds in accordance with 544.1.1.
That NIC document is in relation to EICR rather than installation.
We had a site temporary supply connected up to PME last week. One of our lads had driven a rod in the ground and then for some reason left a 16mm out with the tails as well. Meter guys connected it up to PME.
Nick
 27 May 2017 05:53 PM
weirdbeard
Thanks for the reply nick, could you quote that bit from leckies linked page, can't find it?
The only mention of Pme is
"TN-S was the default earthing system pre-1978 before PME became commonplace."
:beer)
 27 May 2017 06:07 PM
John Peckham
Weirdbear
In answer to your question above, "What's a stroma? "
I think it refers to Stroma Certification one of the government approved competent person schemes just like NICEIC and NAPIT.
You can find details here, LINK
John Peckham
 27 May 2017 08:05 PM
weirdbeard
Originally posted by: John Peckham
Weirdbear
Thanks John, though do stromas have any powers to supercede BS7671?, if it looks like TNS then it isn't PME!
:beer)
 27 May 2017 08:22 PM
NMBelectrical
My apologies Weirdbeard, I got my articles crossed, it was the stroma article that stated that. Its available on the PE website.
Nick
 27 May 2017 09:52 PM
Zoomup
Yep. P.M.E. is the preferred type of earthing supplied (if permissible) by U.K.P.N. http://www.ukpowernetworks.co....ur-services/earthing/
Z.
 27 May 2017 10:14 PM
John Peckham
Weirdbeard
In what way do you think that Stroma has superseded BS7671? Have you read the article?
John Peckham
 27 May 2017 10:33 PM
John Peckham
I found a link to the article
PE LINK
">http://professional-electricia...roma-what-on-earth/[/S</a>
Sorry I cannot get the link to work, Just Google Professional Electrician Magazine May 2017, then select "Features" and then the "Page 2" tab it is called "What on Earth".
John Peckham
Edited: 27 May 2017 at 10:41 PM by John Peckham
 28 May 2017 01:12 AM
geoffsd
 28 May 2017 04:38 AM
spinlondon
It's not a matter of BS7671 being superseded, it's a matter of compliance with BS7671.
The requirement refers to "where PME conditions apply".
PME conditions could apply where an installation is TN-S or TT, not just where an installation is TN-C-S.
 28 May 2017 04:11 PM
weirdbeard
No further comment, cheers
:beer)
 28 May 2017 04:20 PM
weirdbeard
http://
]http://professional-electrician.com/features/stroma-what-on-earth/">PE LINK</a>
Item 2 of the forums conditions auto prevents links deemed not to satisfy the following: "The discussion areas may not be used for the promotion of products and services of any kind, nor for recruitment advertising; potential advertisers are invited to contact our Advertising Department. However, this condition should not discourage users from suggesting a product that may assist a genuine enquirer who has raised a specific problem. In such circumstances, users should obey the custom among professional engineers of declaring any interest.
Your best bet is fudge the link and let someone else correct it
:beer)
 28 May 2017 04:42 PM
John Peckham
Weibeard
NMB Electrical directed you to the source of the information. I attempted to insert a link to the article in PE Magazine but it did not work. I was not promoting PE Magazine just referencing the source of the information in the same way as you posted a link to a web site above.
It is a pity you have declared that you will make no further comment on the subject as I would be interested in yours and others points of view.
John Peckham
Edited: 28 May 2017 at 04:50 PM by John Peckham
 28 May 2017 08:38 PM
weirdbeard
Weibeard
Hi john, to be fair I think the OP has misinterpreted this bit of the link as meaning that they dont need to know about the existing earthing arrangements nor bother attempting to find out, just need to apply table 54.8 everywhere:
"Whilst DNOs are under a statutory duty to confirm the means of earthing to consumer's installations, this may be difficult and time-consuming to verify."
:beer)
 28 May 2017 09:19 PM
weirdbeard
I think it's the same STOMA mentioned here:
http://www.theiet.org/forums/f...d=205&threadid=103149
Or the stoma mentioned here
http://www.theiet.org/forums/f...tid=205&threadid=39960
:beer)
 28 May 2017 11:56 PM
spinlondon
Yes.
STROMA*