hi guys just watched the niceic dvd on inspection & test and in it they measured a Ze of 0.69 and tony cable said that for a tncs system this was ok as they were "in the sticks" what happened to a max of 0.35 ohms that i've been using for the last 20 years
cheers guys |
|
|
|
|
|
|
|
|
Since when has a limit on Ze determined what earthing arrangement exists.
The value of 0.35 ohm simply comes of an engineering guidance note - it's a probable upper value for a domestic supply(TN-C-S), there is no "max" about it. Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
i thought 0.35 ohms was the limit on tncs or you have to call supplier saying theres a problem? Thats what i was taught anyway
|
|
|
|
|
|
|
|
|
LoL - OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
was it right or wrong oms please
|
|
|
|
|
|
|
|
|
Well, not wrong per se - but not correct either.
There is no upper limit to a TN-C-S supply (or to any other earthing arrangement). Values exceeding 0.35 ohm in a small installation might suggest there is a developing problem but equally it might just be that you are a long way from a transformer in a lightly serviced section of the network. All you need to ensure is that Ze is sufficiently low to operate your selected protective devices and that if it is actually a PME supply that you have sized the bonding correctly. The stability of Ze is probably more important than the specific value Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Thanks alot oms its appreciated
|
|
|
|
|
|
|
|
|
Although it might imply a maximum supply of about 53.3A if the supply voltage limits (+10%/-6%) are to be kept within. - Andy. |
|
|
|
|
|
|
|
|
When I spoke to WPD quite a while ago, they said that for an overhead supply for TN-C-S they would accept values up to 0.80 Ohms.
------------------------- Regards Carl. |
|
|
|
|
|
|
|
|
The values of loop impedance in Electricity Association Engineering P23/1 are indicative values for the majority of installations whether they use PME or other forms of earthing. They are not maximum values permitted for provision of PME. P23/1 provides a typical maximum value of LV network loop impedance (eg 0.35 ohm for supplies up to 100 amps) with the caveat: 'Higher values could apply to consumers supplied from small capacity pole transformers and/or long lengths of low voltage overhead lines.' OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Why would you go to the niceic, or the "wiring regs" for advice on
a distributors network? The external loop impedances are: 100 amp=0.38 80 amp=0.56 60 amp=0.72 Trust me. |
|
|
|
|
|
|
|
|
Why would you go to the niceic, or the "wiring regs" for advice on a distributors network? The external loop impedances are: 100 amp=0.38 80 amp=0.56 60 amp=0.72 Trust me. ???????? - how can you give definitive values for a network, it would appear that you are simply applying ESQCR maximum voltage tolerance of +10%,-6% to derive Ze on a TN-C-S system (incorrectly it would appear - I suspect the latter figures should be 0.46 ohm for the 80A service and 0.61 for the 60A service.) Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|
|
|
|
Pmenetwork,
Are those Ze values you quoted only theoretical values. Take one example a housing site recently supplied by aerial bundled cables between houses + one quarter mile to sub station, (PME). Ze on last house = 0.9 ohms. This example may be the same all over the country where long runs of overheads are installed, to comply with your readings a transformer on a pole would need to be plonked in every ones back garden (exaggerated but some validly). On my list of disconnection times of 0.4 & 5 seconds Ze for 100A BS 88 is 0.42 ohms. Maximum Ze & Zs Values BS 88-2.2 & BS 88-6 gG Fuses 5A : n/a 6A : 0.4s = 8.52, 5s = 13.5 10A : 0.4s = 5.11, 5s = 7.42 15A : n/a 16A : 0.4s = 2.70, 5s = 4.18 20A : 0.4s = 1.77, 5s = 2.91 25A : 0.4s = 1.44, 5s = 2.3 30A : n/a 32A : 0.4s = 1.04, 5s = 1.84 40A : 0.4s = n/a, 5s = 1.35 45A : n/a 50A : 0.4s = n/a, 5s = 1.04 60A : n/a 63A : 0.4s = n/a , 5s = 0.82 80A : 0.4s = n/a , 5s = 0.57 100A : 0.4s = n/a , 5s = 0.42 125A : 0.4s = n/a , 5s = 0.33 160A : 0.4s = n/a , 5s = 0.25 200A : 0.4s = n/a , 5s = 0.19 Regards jcm |
|
|
|
|
|