Topic Title: Internal Cavity wall Topic Summary: Am I allowed to use it ? Created On: 25 February 2010 06:33 PM Status: Post and Reply |
Linear : Threading : Single : Branch |
Search Topic |
Topic Tools
|
|
|
|
|
Evening ,
Carrying out a rewire this week , The old cables are fed through a internal cavity wall into the DB , Can I use the same route ? Mains tails will be surface . cheers |
|
|
|
|
|
|
|
|
Why do ou think you wouldnt be able to?
regards Misterben |
|
|
|
|
|
|
|
|
Thought I read some where cables in cavitys a big no no ?
|
|
|
|
|
|
|
|
|
cables less than 50mm in a wall? within safe zones?
regards Misterben |
|
|
|
|
|
|
|
|
Guidance from the Electricity Safety Council says "installing such cables in this way (external cavity walls) is generally an undesirable practice"
The reasons give are 1. Obstructions in a cavity wall, such create a risk of unseen damage during installation. 2. Long unsupported vertical drops may place undue strain on the conductors, leading to damage 3. Polystyrene used for insulation, if it come into contact with thermoplastic (pvc) cable sheathing, plasticiser can migrate from the thermoplastic to the polystyrene 4. Thermal insulation in the cavity may cause cable not to be able to carry the load current without overheating due to their current-carrying capacity being reduced 5. Presence of flora and fauna - unforeseen external influences There is also a requirement in the Building Regulations 2000, Approved Document C, 2004 Edition, Section 5: Walls, paragraph 5.13 b and NHBC Standards state that no cables other than electricity meter tails are to be located in the cavity of an external wall |
|
|
|
|
|
|
|
|
Its a drop of about half a meter
I will have to chop the lounge wall out then i suppose Go back entry that way . |
|
|
|
|
|
|
|
|
I think ampman is talking about a few feet of cable routing throught to a DB?
I had to move a DB and dropped cabling about two feet from ceiling into cavity directly into DB. The customer wouldnt want surface trunking or their wall chopped out. As for the derating issue that has been raised before i.e cable covered in insulating foam; is this first few feet of a 30-40 feet run going to really affect the cables current carrying capacity? I think not regards Misterben |
|
|
|
|
|
|
|
|
Cheers Misterben ,
Didnt think of it like that its only a drop of a few feet from upstairs underfloor boards into DB located within the porch . I will carry on now Thanks |
|
|
|
|
|
|
|
|
Guidance from the Electricity Safety Council says "installing such cables in this way (external cavity walls) is generally an undesirable practice" The reasons give are 1. Obstructions in a cavity wall, such create a risk of unseen damage during installation. - dont we test for these before we energize? 2. Long unsupported vertical drops may place undue strain on the conductors, leading to damage - agree with this, but for a metre ? 3. Polystyrene used for insulation, if it come into contact with thermoplastic (pvc) cable sheathing, plasticiser can migrate from the thermoplastic to the polystyrene 4. Thermal insulation in the cavity may cause cable not to be able to carry the load current without overheating due to their current-carrying capacity being reduced- as i said above 5. Presence of flora and fauna - unforeseen external influences There is also a requirement in the Building Regulations 2000, Approved Document C, 2004 Edition, Section 5: Walls, paragraph 5.13 b and NHBC Standards state that no cables other than electricity meter tails are to be located in the cavity of an external wall It all seems like another way of making electricians lifes difficult, half of the rules now that were supposed to implement are way over the top in my opinion regards Misterben |
|
|
|
|
|
|
|
|
and NHBC Standards state that no cables other than electricity meter tails are to be located in the cavity of an external wall
------------------------------------------- But the OP isn't building a new house so what have they got to do with it? Dave. |
|
|
|
|
|
|
|
|
Correct, just seems like another example of people forgetting their basic electrical theory and or allowing it to be clouded by too many misguided opinions and the big red book
regards Misterben |
|
|
|
|
|
|
|
|
I was simply quoting the ESC guidance, the OP is better informed and can take from it what it wants, alternatively he could read Alan Lynch's book "the part P doctor", Alan pretty much refutes all the the claims and is OK with cables in external cavity walls.
Its only guidance the OP will need to make his own mind up. |
|
|
|
|
|
|
|
|
Are you talking about a cavity between the exterior wall and the interior wall or a cavity to an internal wall?
Do not install cables within external cavity walls. The cavity is there for a reason and its not for running cables. |
|
|
|
|
|