Topic Summary: Any regs on distances?
Created On: 24 February 2010 09:27 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 24 February 2010 09:27 PM
User is offline View Users Profile Print this message



kitleach

Posts: 62
Joined: 19 August 2009

Are there any minimum distances that must be met seperating the cooker gas hob from its hood?

I can't find anything myself, Section 422 seems to let you use your own judgement.

Does anyone use a rule of thumb on this? Normally I like to install them as far appart as possible (or if that looks ridiculous as far appart as aesthetics allow), however I have just looked at a job and the ducting for the hood is only about 3 foot above the hob, so the hood would be even closer than that.

I would be greatful for any advice.

Thank you
 24 February 2010 09:29 PM
User is offline View Users Profile Print this message



CarlCosby

Posts: 484
Joined: 16 March 2009

Manufacturers instructions?

-------------------------
Regards
Carl
 24 February 2010 09:35 PM
User is offline View Users Profile Print this message



alancapon

Posts: 5745
Joined: 27 December 2005

With a gas hob, the answer to this one is more likely to be found in some of the gas regulations.

Regards,

Alan.
 24 February 2010 09:41 PM
User is offline View Users Profile Print this message



Chris123

Posts: 306
Joined: 08 February 2010

Where manufactures info is not available and a gas hob height is 760mm

Edited: 25 February 2010 at 09:47 AM by Chris123
 24 February 2010 11:10 PM
User is offline View Users Profile Print this message


Avatar for RRichard.
RRichard

Posts: 1406
Joined: 11 January 2005

Originally posted by: Chris123

Where manufactures info is not available and a gas hob height is 750mm



Thats correct. I had to look this up with the GasSafe 'engineer' in his bible only this Monday.
 25 February 2010 12:25 AM
User is offline View Users Profile Print this message


Avatar for Dale76uk.
Dale76uk

Posts: 412
Joined: 04 February 2010

You'll find this information in the Electricians Guide to the Building Regulations (Green Book)
 25 February 2010 09:47 AM
User is offline View Users Profile Print this message



Chris123

Posts: 306
Joined: 08 February 2010

Just checked the gas reg book its 760mm to underside of hood
 25 February 2010 10:22 PM
User is offline View Users Profile Print this message



kitleach

Posts: 62
Joined: 19 August 2009

Thanks everyone. Very helpful