If a switch cable runs vertically up a wall from the switch and enters the ceiling, is that cable considered unprotected from the point at which it enters the ceiling to a point where it is above 50mm from the bottom of the ceiling joist? Is it assumed that the safe zone formed upwards from the switch extends a short distance into the ceiling or should we be protecting this short section of cable?
|
|
|
|
|
|
|
|
|
I would say that if the cable is <50mm from any surface then it requires protection?
|
|
|
|
|
|
|
|
|
Are we now saying that we need to put in 2 inches of earthed steel conduit above the ceiling? don't be daft!
Dave. |
|
|
|
|
|
|
|
|
I believe that the cable enters a safe zone some 150mm from the ceiling on a vertical run.
|
|
|
|
|
|
|
|
|
I believe that the cable enters a safe zone some 150mm from the ceiling on a vertical run. I second that. |
|
|
|
|
|
|
|
|
OJ is questioning whether or not that safe zone extends above the ceiling!
|
|
|
|
|
|
|
|
|
why not use mechanical protection from the switch/socket which enters 50mm above the ceiling??? I've always done this.
|
|
|
|
|
|
|
|
|
The requirement is for the cable to be protected from nails and screws, where it passes through a joist.
I don't think it is considered likely that someone will put nails and screws in between joists. |
|
|
|
|
|
|
|
|
Following an assessment of the likely damage to occur to the said 50mm above the ceiling...
Come on guys is it likely that a picture is going to go within the floor joist. As for protection I am yet to see any installed so as to negate the use of rcd's capping ..yes but its not mechanical protection is it? ------------------------- Regards Martyn. Only a mediocre person is always at their best www.electrical contractors uk.com |
|
|
|
|
|
|
|
|
why not use mechanical protection from the switch/socket which enters 50mm above the ceiling??? I've always done this.
-------------------------------------- And how do you do that Dale? 50mm of earthed steel conduit? ridiculous. Nothing else will provide mechanical protection, steel capping for instance isn't regarded as mechanical protection. |
|
|
|
|
|
|
|
|
If a switch cable runs vertically up a wall from the switch and enters the ceiling, is that cable considered unprotected from the point at which it enters the ceiling to a point where it is above 50mm from the bottom of the ceiling joist? Is it assumed that the safe zone formed upwards from the switch extends a short distance into the ceiling or should we be protecting this short section of cable? No it is not : read 522.6.5 more carefully. The 50mm stipulation only applies when passing through a joist. Apart from that you should 'run in such a position that it is not liable to be damaged by contact with the .. ceiling or their fixings' directly above a wall at any height would comply. |
|
|
|
|
|